Home Page link

my neighbor is using my neutral wire, is he stealing my electricity? - Page 2

Building Construction - Building Construction Industry Discussions. 

Page 2 of 2       << first < 1 2 Bookmark this page:  YahooMyWeb Yahoo!  Google Google  Windows Live Favorites Windows Live  del.icio.us del.icio.us  digg digg  Add to Netscape Netscape
Subject Author Date
my neighbor is using my neutral wire, is he stealing my electricity? Stan 08-25-2009
If you were  Registered and logged in, you could reply and use other advanced thread options
Posted by PeterD on August 27, 2009, 8:41 am


On Wed, 26 Aug 2009 22:33:29 -0500, "Grasshopper" <NONE> wrote:

>> Stan wrote:
>> > I know this is crazy, but I live in a duplex, that at one point was
>> > combined to be a big house, and now it's a duplex again. So the
>> > electricity at one point had 2 meters, then it had one meter, now it
>> > has 2 meters again.
>> > The electrical works perfect, but now I am trying to add another
>> > electrical outlet. However, I found out that my neighbor, who is on a
>> > different electrical meter, is feeding off my neutral wire. He is not
>> > feeding off my hot wire, just the neutral. This has been going on for
>> > over 15 years. I can move the neutral over to his meter, but it will
>> > take me a few hours. As long as he is not feeding off my electricty,
>> > I don't care, What do you think I should do?
>> Call an electrician. You and your neighbor obviously need one.
>> Seriously, if you don't understand hot and neutral and they work you
>> need to get someone who does.
>> --
>> Art
>I understand hot and neutral. I even changed a whole circuit breaker
>from fuse to breakers. Let me tell you what I did so far.....
>First, my meter and my neighbors meter are right next to each other. I
>opened up my meter

You cannot open a meter in any location I know of, without violating
both the agreement between you and the supplier, and usually
local/state laws. Tampering with the meter (opening it constitutes
tampering) is a criminal offense. Not the best move.

>and noticed that I have 6 neutral wires running
>out. (I should only have 3.)

Why three? Two hot, one neutral.

>Then I opened my neighbors meter

See the above on tampering with power meters...

>and he
>had zero neutral wires running out. (He should have 3.)

See the above on why three.

> I followed 3
>of the neutral wires and it went to his unit. However, to make sure, i
>disconnected all six of my neutral wires.

OK, clearly you jumped off the deep end. And, into water the depth of
which was unknown to you. Disconnecting neutrals can easily damage the
applicances on the power system as there is nothing to ensure that
they receive the proper loads.

>I then went to his unit and
>found out that 1/4 of his circuit was dead.

How did you find 25% of his circuits were dead? Like breaking into the
meters, did you break into his house?

>However, the other 3/4 are
>still getting the neutral from somewhere.

There is nothing to indicate that. What you did was possibly damage
his appliances due to unbalanced voltages resulting from an open
neutral.

> I don't know where. It's
>strange because although 3/4 of his circuits are still working, all
>the neutrals from both units are disconnected.

The only thing clear here is that you have no clue how power supplied
to residential circuits works. You are dangerous, I do hope you don't
kill someone, or burn down someone's house.

> I then checked my house
>and all the electricity was dead. After this I hooked up his 3 neutral
>wires all his electricity is back to normal. Then I hooked up my 3
>neutral and my electricity is back to normal also.

Well, 'normal' is relative. You don't say what, where or how you
reconnected the neutrals.

You are a lucky man, you survived (I think) this little adventure.
Lifting the neutrals on a live circuit can be fatal, I hope you
realized that. They are only neutrals as long as they are connected
(properly) and once you lift them, they become hot conductors, and can
have line voltages on them.

>__________________________________________
>__________________________________________
>Entirely different universe than mine. In the universe I live, the
>resident, servicing electrician or whoever, cannot open a meter that
>measures the electrical use of a residence or business. The electricity
>provider owns that equipment. Its all AC, there is no grounding or neutral
>at the meter itself.
>The universe I live in, the grounding and neutral are provided after the
>meter.
>What you're saying is all alien to me.

Alien? Hell, the OP is one lucky bastard-I'm amazed he lived to tell
the story, and as soon as the meter reader sees the damaged meter
seals he'll regret opening the boxes. At a minimum they will send a
line truck to open, inspect for tampering, reseal, and recalibrate and
that will be a charge for item!

(Grasshopper: your newsreader needs to be properly configured to
handle quotes in replies... It is virtually impossible to see where
the OP posted, and you replied. There are standards for posting, sadly
it appears that MSFT hs violated these rules. I'd recommend you get a
copy of either Agent, or Thunderbird, and scrap OE...)

Posted by Art on August 27, 2009, 8:57 pm


Stan wrote:
>> Stan wrote:
>>> I know this is crazy, but I live in a duplex, that at one point was
>>> combined to be a big house, and now it's a duplex again. So the
>>> electricity at one point had 2 meters, then it had one meter, now it
>>> has 2 meters again.
>>> The electrical works perfect, but now I am trying to add another
>>> electrical outlet. However, I found out that my neighbor, who is on a
>>> different electrical meter, is feeding off my neutral wire. He is not
>>> feeding off my hot wire, just the neutral. This has been going on for
>>> over 15 years. I can move the neutral over to his meter, but it will
>>> take me a few hours. As long as he is not feeding off my electricty,
>>> I don't care, What do you think I should do?
>> Call an electrician. You and your neighbor obviously need one.
>> Seriously, if you don't understand hot and neutral and they work you
>> need to get someone who does.
>> --
>> Art
>
> I understand hot and neutral. I even changed a whole circuit breaker
> from fuse to breakers. Let me tell you what I did so far.....
>
> First, my meter and my neighbors meter are right next to each other. I
> opened up my meter and noticed that I have 6 neutral wires running
> out. (I should only have 3.) Then I opened my neighbors meter and he
> had zero neutral wires running out. (He should have 3.) I followed 3
> of the neutral wires and it went to his unit. However, to make sure, i
> disconnected all six of my neutral wires. I then went to his unit and
> found out that 1/4 of his circuit was dead. However, the other 3/4 are
> still getting the neutral from somewhere. I don't know where. It's
> strange because although 3/4 of his circuits are still working, all
> the neutrals from both units are disconnected. I then checked my house
> and all the electricity was dead. After this I hooked up his 3 neutral
> wires all his electricity is back to normal. Then I hooked up my 3
> neutral and my electricity is back to normal also.

You're question implies that you don't understand hot and neutral. You
certainly you don't understand how this is wired, you just admitted it.
Get an electrician.

--
Art

Posted by F Murtz on August 28, 2009, 11:34 am


Stan wrote:
>> Stan wrote:
>>> I know this is crazy, but I live in a duplex, that at one point was
>>> combined to be a big house, and now it's a duplex again. So the
>>> electricity at one point had 2 meters, then it had one meter, now it
>>> has 2 meters again.
>>> The electrical works perfect, but now I am trying to add another
>>> electrical outlet. However, I found out that my neighbor, who is on a
>>> different electrical meter, is feeding off my neutral wire. He is not
>>> feeding off my hot wire, just the neutral. This has been going on for
>>> over 15 years. I can move the neutral over to his meter, but it will
>>> take me a few hours. As long as he is not feeding off my electricty,
>>> I don't care, What do you think I should do?
>> Call an electrician. You and your neighbor obviously need one.
>> Seriously, if you don't understand hot and neutral and they work you
>> need to get someone who does.
>> --
>> Art
>
> I understand hot and neutral. I even changed a whole circuit breaker
> from fuse to breakers. Let me tell you what I did so far.....
>
> First, my meter and my neighbors meter are right next to each other. I
> opened up my meter and noticed that I have 6 neutral wires running
> out. (I should only have 3.) Then I opened my neighbors meter and he
> had zero neutral wires running out. (He should have 3.) I followed 3
> of the neutral wires and it went to his unit. However, to make sure, i
> disconnected all six of my neutral wires. I then went to his unit and
> found out that 1/4 of his circuit was dead. However, the other 3/4 are
> still getting the neutral from somewhere. I don't know where. It's
> strange because although 3/4 of his circuits are still working, all
> the neutrals from both units are disconnected. I then checked my house
> and all the electricity was dead. After this I hooked up his 3 neutral
> wires all his electricity is back to normal. Then I hooked up my 3
> neutral and my electricity is back to normal also.


If someone gets killed in those units guess who goes to jail.

Posted by PeterD on August 26, 2009, 8:29 am


wrote:

>Stan wrote:
>> I know this is crazy, but I live in a duplex, that at one point was
>> combined to be a big house, and now it's a duplex again. So the
>> electricity at one point had 2 meters, then it had one meter, now it
>> has 2 meters again.
>>
>> The electrical works perfect, but now I am trying to add another
>> electrical outlet. However, I found out that my neighbor, who is on a
>> different electrical meter, is feeding off my neutral wire. He is not
>> feeding off my hot wire, just the neutral. This has been going on for
>> over 15 years. I can move the neutral over to his meter, but it will
>> take me a few hours. As long as he is not feeding off my electricty,
>> I don't care, What do you think I should do?
>Call an electrician. You and your neighbor obviously need one.
>Seriously, if you don't understand hot and neutral and they work you
>need to get someone who does.

And Stan:

Last I remember, neutral is not metered. Not to say what you have is
OK, it is not (in fact it is outragous to have it wired that way) but
I would not say it was stealing your power. Have an electrican come
and fix the wiring--no this is not a typical home improvement, and yes
you will be cutting his power when you do this.

Caution: if you do this yourself, you take the risk of causing serious
damage to electrical devices on the circuts in question. Use an
electrican, who must have access to both breaker panels, and
cooperation with the other resident(s).

Posted by Cwatters on August 28, 2009, 10:34 am



>I know this is crazy, but I live in a duplex, that at one point was
> combined to be a big house, and now it's a duplex again. So the
> electricity at one point had 2 meters, then it had one meter, now it
> has 2 meters again.
> The electrical works perfect, but now I am trying to add another
> electrical outlet. However, I found out that my neighbor, who is on a
> different electrical meter, is feeding off my neutral wire. He is not
> feeding off my hot wire, just the neutral. This has been going on for
> over 15 years. I can move the neutral over to his meter, but it will
> take me a few hours. As long as he is not feeding off my electricty,
> I don't care, What do you think I should do?

Tampering with someones electricity supply would get you in big trouble
where I live.

I supect you don't have the equipment to test the end result properly.



Page 2 of 2       << first < 1 2
Similar ThreadsPosted
how to know if unknown wire is "neutral or ground"? August 26, 2009, 10:49 pm
Introducing The Hz2.1 Portable Hot Stamp Wire Marker to Meet Industry's Need for Flexible, Cost-effective Wire Marking April 30, 2007, 4:07 pm
sell building material ,wire mesh ,welded wire mesh December 24, 2006, 12:26 am
Saving electricity. in Re: Doorbell always uses electricity! November 21, 2008, 10:18 am
Saving electricity. in Re: Doorbell always uses electricity! November 21, 2008, 11:10 am
Electric question - hot neutral September 18, 2007, 8:55 pm
help on neutral and ground 480 volt December 2, 2008, 2:03 pm
Are all neutral wires in 120 volt residential shared? August 12, 2009, 10:51 pm
Submersible wire instead of UF October 3, 2009, 12:59 am
sell wire mesh December 6, 2006, 1:46 am

Contact Us | Privacy Policy

XML SitemapXML Sitemap