Posted by RBM on March 30, 2007, 7:09 am
The current code wouldn't apply to a preexisting condition. Essentially he's
just changing the receptacle for a GFCI type which is fine
>> No, nothing wrong with that. Just make sure the terminals are tight on
>> the
>> wires. My preference is to splice the wires together with pigtails to the
>> outlet
>>
>>
>>
>>
>>
>> > I'm putting a GFCI in a bathroom. Ideally I would use the load
>> > terminals
>> > and protect the other outlets downstream too. Unfortunately down line
>> > from
>> > the GFCI is a refrigerator. I don't want the fridge on a GFCI circuit
>> > because they occaisionally phantom trip and I don't want a bunch of
>> > spoiled food. The GFCI has 4 terminals for Line, 2 neutral and 2 hot
>> > and 4
>> > terminals for load 2 neutral and 2 hot. Is there any reason including
>> > the
>> > NEC that the load wires cannot just be wired to the extra line
>> > terminals
>> > to bypass the GFCI and allow power to the fridge even if the GFCI
>> > trips?
>> > Yes I understand none of the outlets after the GFCI will be protected
>> > as
>> > they would be if they were wired to "load", and I will take care of
>> > that
>> > when I add GFCI to the kitchenette where the fridge is in whatever way
>> > will work best depending on exactly where, electrically speaking, in
>> > the
>> > daisy chain the fridge outlet is. The GFCI is one of the idiot proof
>> > ones
>> > that comes tripped and supposedly won't reset until it's correctly
>> > wired.
>> > Testing it out it works fine wired this way as far as the test and
>> > reset
>> > buttons on it go. Is there any practical reason, including the NEC,
>> > not
>> > to do it this way? I appreciate good responses but please don't answer
>> > if
>> > you don't know anything about wiring or are wondering what NEC, load or
>> > line means.
>>
>> > Thanks.- Hide quoted text -
>>
>> - Show quoted text -
>
> As RBM states what you are suggesting will work. However, per current
> code a bathroom circuit shouldn't be supplying anything outside a
> bathroom.
>
|