Posted by Ignoramus18798 on May 22, 2006, 11:12 am
> On Mon, 22 May 2006 13:58:15 GMT, Ignoramus18798
>
>>>
>>>>I presently have a 220V subpanel in my garage, the circuit is wired
>>>> with 6 gauge wire on a 60A circuit breaker.
>>>>
>>>> This circuit is inside a 3/4" conduit. It is comprised of three 6
>>>> gauge wires (two hots and neutral, with conduit being the ground).
>>>>
>>>> I now realize that choosing that low capacity was a mistake. (with a
>>>> big welder now in the picture) I would like to know just what would be
>>>> involved if I wanted to upgrade to 100A.
>>>>
>>>> Can I be able to squeeze, say, two 4 gauge conductors (hots), plus one
>>>> 8 gauge conductor (neutral), into a 3/4" conduit? Or will I have to
>>>> replace the conduit too?
>>>>
>>>> I am very regretful of not doing the right thing and going for max
>>>> capacity. When I did it, the only 220V tool I had was a 3 HP
>>>> vertical compressor.
>>>>
>>> Can't answer your question (at least not without looking it up...) but
>>> wonder if you have the electrical capacity in your panel for a 100a sub.
>>
>>Good question.
>>
>>I have a 200A panel. The big loads that I may have is a 28A air
>>conditioner and a 50A kitchen range.
>>
>>The garage circuit is used for my hobby stuff (compressor, welder),
>>and, as such, is used very intermittently. As you can guess, the
>>welder is also going to be used at a low duty cycle, it is not a
>>production style situation.
>>
>>That's some data for me to ponder.
>>
>>i
>
>
> You could possibly squeeze two 4s and an 8 in 3/4" (39% fill) but if
> there are many bends you will have trouble getting them in there.
The bends that I have are all open kind, that is, there is either a 90
degree turn with removable back cover, or a junction box.
> That still only gets you 85 amps that you can "round up" to a 90a
> breaker. 310.15(B)(6) does not apply to sub panels.
> On the other hand, I wouldn't do anything until I had a problem.. I
> ran a pretty big shop with a welder and AC on a 60a.
Thanks... Maybe I will just follow your advice. I am not going to weld
bridge sections or oceangoing ships.
i
|